Ground Rod to Foundation Distance?

Status
Not open for further replies.

JKR

Member
Anyone, does code state a minimum required distance from a ground rod to the foundation of the building for any type of application? Thx
 
But the footing itself may keep you at a distance from the wall. Usually, a footing is twice the wall thickness, so an 8" block or brick-n-block foundation should have a 16"-wide footing. That would mean at least 4" of footing outside the foundation wall.
 
option 86

option 86

No, I do not believe there is a code restriction even if the rod is direct buried horizontally over the footer pour if it is deep enough. rbj
 
For a driven electrode, its to be in permanent moisture if practicable. So if you can get it out away from the foundation, that will lower the resistance somewhat.
 
Status
Not open for further replies.