To bury the 8 foot rod does not comply to the concrete encased electrode.(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (? in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means.
As long as the rod is 30 inches deep I don't see anything wrong with it being under the pad.250.53(G) the electrode shall be permitted to be buried in a trench that is at least 750 mm (30 in.) deep
Of what code section?Having the rod exposed like that is an actual violation
I had an inspector that insisted that the connection to the rod had to be available for maintenance. I drove it even further down and placed a four inch plastic pipe over it with a female connector and a threaded plug. He was not a happy camper but I asked him to write it up so I could get the money for the extra work and he backed off. I then learned that the home owner was going to run a business involving computer servers and T1 line out of the home. So I installed rod couplers and stacked on two more rod sections until I got down to less than five ohms. I told the owner that what he did with that ugly piece of pipe was his business. I suspect he removed it but since he could do that without disturbing the GEC I can't see that it would do any harm.Originally posted by jes25:
About half the rods I see stick up about an inch. One guy told me to do it like that so the inspector could see it. :roll:
You know what happens when they mow the lawn.![]()