Engineer calls for (3) 3/4" x 10' copperclad ground rods for a 1600A service.  I've been going through the codes, and some google searches... but I would like to know why the need for a 3/4" x 10' rod is suggested (or is it required?)?  I did find a 10 year old article... https://forums.mikeholt.com/threads/size-of-ground-rod.67325/  Does anyone have any new information?
Looking at code... 250.52(A)(5) - Rods and pipes shall not be less than 8', pipes or conduit shall not be smaller than 3/4", and rods shall be at least 5/8".
	
		
			
		
		
	
				
			Looking at code... 250.52(A)(5) - Rods and pipes shall not be less than 8', pipes or conduit shall not be smaller than 3/4", and rods shall be at least 5/8".
 
				
 
 
		 
 
		 
 
		 
 
		 
 
		 
 
		