Ground Rods at Light Poles

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
250.32(A) tells us it is not required. I keep encountering people who cling to the urban legend that they, somehow, provide a necessary protection. I can make the case for a shock hazard, given that the EGC, and not the ground rod, provides protection. But what about lightning strikes? I am debating one person who cites instances in which lightning struck a light pole that did not have a ground rod, and citing the damage that the pole suffered. I want to counter-claim that the presence of a ground rod would not have altered the results, would not have prevented or even reduced the damage.

Am I right? Does anyone have any real-life evidence to back my point of view?
 
I once attended a Mike Holt class, and he ridiculed the idea that a ground rod would make a difference.
 
I think you need to measure resistance with and without the rod, or if rod is in the concrete at two different poles but with similar base design in similar soil type.

small posts with luminaires may not have much of a base but parking lot lights and such on 20' plus poles will have big enough base that just the rebar in the base makes just as good if not better electrode than a single rod does IMO, even if it doesn't quite meet the NEC requirements of a CEE.
 
Charlie, if lightning makes a direct hit there is no way a rod will reduce the damage or even reduce the damage enough to make a difference. I have seen a house get hit that had chemical ground rods installed around the perimeter of his home but he lightning still got all his electronics. A direct hit is one thing but a hit from a surge is another. I am not sure a rod would help much but I guess there is a point at which it could.....
 
Charlie, if lightning makes a direct hit there is no way a rod will reduce the damage or even reduce the damage enough to make a difference. I have seen a house get hit that had chemical ground rods installed around the perimeter of his home but he lightning still got all his electronics. A direct hit is one thing but a hit from a surge is another. I am not sure a rod would help much but I guess there is a point at which it could.....
another good point, direct hits usually going to be some damage regardless what kind of electrode or resistance it has
 
Do most light poles not have concrete footing with rebar?

Ground rods come from the day when it was thought that soil did everything besides turning the prime mover.
 
I had a customer that lived on top of a hill, lighting continuously took out his fence charger. He was at the end of the poco line. Drove three ground rods at the house, three at the barn, and three at the last poco pole. He has had no more issues. Had another one below a rock quarry that every time a storm would come up, it would blow out his phones and tv’s, drove two more rods at his service, buried a bare copper wire in the yard to bond the phone and TV lines to the service (phone and tv came in at the other end of the house). No more problems. Most likely the surges were coming in from the cable and phone, and since they weren’t bonded to the service, I believe that was the biggest issue.
 
Do most light poles not have concrete footing with rebar?

Ground rods come from the day when it was thought that soil did everything besides turning the prime mover.
Yeah, and usually the ground rod is just thrown into the pour, and not even tied to the rebar, so doesn’t really do a whole lot of good.
 
I recall an article from a power utility a long time ago that suggested that where they had concrete pole bases, they could reduce the damage to the concrete from a lighting strike to the pole by adding a ground rod outside the pole base or by doubling up on the wire ties used to secure the re-bar. Not sure of the actual source and if there were any actual studies on the issue. They suggested that the damage to the pole base was from the lighting current turning the moisture in the concrete into steam and the volume expansion of ~1700 would damage the concrete.
 
Once you are discussing lightning actually striking the pole, I don't think you can have a useful discussion on the basis of theory. The best you could do is find an actual study of events, for example if the article mentioned in post #9 actually had pole base damage stats.

As a related aside about how powerful a lighting strike can be:
A couple of days ago I learned that small fraction of lightning strikes accelerate electrons enough to cause gamma emission, to the extent of detectable levels of nuclear activation (the gamma rays are energetic enough to knock neutrons out of a nucleus, making it radioactive) and pair creation (the gamma rays are energetic enough to hit something and create an electron and a positron). Yes, lightning can in come cases generate very small quantities of antimatter. Given the energy available it is pretty useless to try to argue how lightning will affect a structure based on theory, you need data.


-Jon
 
Once you are discussing lightning actually striking the pole, I don't think you can have a useful discussion on the basis of theory. The best you could do is find an actual study of events, for example if the article mentioned in post #9 actually had pole base damage stats.

As a related aside about how powerful a lighting strike can be:
A couple of days ago I learned that small fraction of lightning strikes accelerate electrons enough to cause gamma emission, to the extent of detectable levels of nuclear activation (the gamma rays are energetic enough to knock neutrons out of a nucleus, making it radioactive) and pair creation (the gamma rays are energetic enough to hit something and create an electron and a positron). Yes, lightning can in come cases generate very small quantities of antimatter. Given the energy available it is pretty useless to try to argue how lightning will affect a structure based on theory, you need data.


-Jon

Question is, does the anti matter do anything?
 

I had a post a while back about local light poles not owned by the utility company, and their need for proper grounding. the above article was something I stumbled upon during my research to confirm the need for proper grounding at light poles.

I did not include lightning into my argument at the time.
 
Question is, does the anti matter do anything?

The small amount of antimatter is in the form of positrons. They pretty much immediately annihilate with a nearby electron to emit a gamma ray. So the only thing this does is cause a bit of gamma 'after-glow' following the initial gamma producing event.

-Jon
 
The small amount of antimatter is in the form of positrons. They pretty much immediately annihilate with a nearby electron to emit a gamma ray. So the only thing this does is cause a bit of gamma 'after-glow' following the initial gamma producing event.

-Jon

Alright, but nothing to do with avagadroes constant, correct? Or actual copper disapering in any sense.
 
I once attended a Mike Holt class, and he ridiculed the idea that a ground rod would make a difference.
There's a great video Mike did, probably similar or the same as you were talking about, where he shows a picture of this giant lighting bolt and he says, "now I don't know if you've done any critical thinking, but if you think a ground rod at the bottom of that light pole is going to do anything......"

Now even if we were to grant that grounding the light poles is advantageous, I would argue the anchor bolts/concrete base/ rebar is already a "ground rod" , you already have one so I don't see what the point of adding another one is.
 

I had a post a while back about local light poles not owned by the utility company, and their need for proper grounding. the above article was something I stumbled upon during my research to confirm the need for proper grounding at light poles.

I did not include lightning into my argument at the time.

That article basically does not have anything to do with grounding electrodes as asked about in the OP.
 