mayanees
Senior Member
- Location
- Westminster, MD
- Occupation
- Electrical Engineer and Master Electrician
I'm involved in a situation where ground rods were specified to be provided at light poles. An inspector has deemed the installation to be non-compliant because it violates 250.53(G) for Rod and Pipe Electrodes because the ditch that the EC has laid the rods in is only 18" deep and needs to be 30" per 250.53(G). I read the section as the rod is required to be driven horizontally or at a 45-degree angle and that if that doesn't work, then in a ditch at 30", but that's for a real grounding electrode.
My contention is that the rods are not required, and therefore they can be placed at the bottom of the 18" ditch. I personally would not have specified rods at light poles per Mike Holt's teachings, but from what I understand the facility wanted them.
So, if the rod is provided at each pole, can they just be laid at the bottom of the 18" ditch that contains the conduits powering the pole light?
Thanks for any responses.
My contention is that the rods are not required, and therefore they can be placed at the bottom of the 18" ditch. I personally would not have specified rods at light poles per Mike Holt's teachings, but from what I understand the facility wanted them.
So, if the rod is provided at each pole, can they just be laid at the bottom of the 18" ditch that contains the conduits powering the pole light?
Thanks for any responses.