If you have building steel and cold water GEC's to the service equipment, do you still need ground rods by code? I'm thinking you don't NEED them. Is there any article that says different?
Take a look at 250.50 and 250.52:smile:If you have building steel and cold water GEC's to the service equipment, do you still need ground rods by code? I'm thinking you don't NEED them. Is there any article that says different?
You do not need them. The water pipe will require one electrode to supplement it. The building steel would comply with that if it's an electrode.
Exactly what I was thinking. I just couldn't find the article that says or allows that. Do you know which one it is by chance?