are ground rods still required if there is a foundation ground for a service ground
rcarroll said:No required, but you still need to bond all grounding electrodes available
brielellalyse said:i read 250.50. but my question is it one or the other or do you need both.
250.50 Grounding Electrode System.
If available on the premises at each building or structure served, each item in 250.52(A)(1) through (A)(6) shall be bonded together to form the grounding electrode system. Where none of these electrodes are available, one or more of the electrodes specified in 250.52(A)(4) through (A)(7) shall be installed and used.
Not only that, I recently had a POCO guyrespond to an open-neutral-at-the-pad-mounted-transformer service call insist that there would have been no problem if the house had "the correct ground rods" installed.don_resqcapt19 said:Check with your utility too...here if you don't have 2 driven rods, they won't hook you up no matter how many other electrodes you have.
Don
LarryFine said:Not only that, I recently had a POCO guyrespond to an open-neutral-at-the-pad-mounted-transformer service call insist that there would have been no problem if the house had "the correct ground rods" installed.
dcspector said:Huh?.................................
My bad.dcspector said:Huh?.................................
from my experince it really comes down to your research with the city's acceptance and knowing your inpector's take on the issue . Even if the print shows ground rods and you take this to your inspector you'llbe better prepared.brielellalyse said:are ground rods still required if there is a foundation ground for a service ground
iwire said:The answer is in 250.50
Beyond a shadow of a doubt, it is a violation.IL94EE said:If I have the opportunity to use the foundation, is it a voilation of code to not use it and just go with a ground rod...?
Not only that, I recently had a POCO guy respond to an open-neutral-at-the-pad-mounted-transformer service call insist that there would have been no problem if the house had "the correct ground rods" installed.