paul
Senior Member
- Location
- Snohomish, WA
On the plus side...it is very sandy soil that I'm driving them into. That brings up another strike against them, but oh well. Maybe I can talk them into some XIT? ground rods and bentonite. :wink:
Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation.
Well, it does give a TVSS something to shoot at...right?iwire said:Forgetting lightning can anyone explain how a connection to earth will limit the voltage applied by 'line surges'?
Not unless the source of the transient voltage is lightning. Even transients must follow the rules and those currents must be returned to their source, not the earth.Well, it does give a TVSS something to shoot at...right?
Gmack said:Line surge can occur without lightning. On grounded systems, loss of the grounded conductor will result in unbalanced voltage traveling above nominal. It can/does cause much damage to equipment down stream.
Gmack said:Having said that, my experience is that lightning does what it damn well pleases anyway.
paul said:Talked to him today. He says that by driving the ground rods, it will increase the lifespan of the electronics inside, which according to him will degenerate over time during electrical storms without a ground rod. Specs say to drive a ground rod to achieve 10 ohms or less to ground. I explained that there is nowhere in the state of WA where you will achieve a ground resistance of 10 ohms or less. But because of the five year warranty and the replacement cost if something should go wrong, I will drive the silly ground rods.
Gmack said:I ask you. Do know that in some parts of the world a 20,000 volt single line is ran to remote housing and they use GROUND RODS/ EARTH to return it back to the sub station.
petersonra said:If you are only putting in the ground rods because the instructions say so, than my suggestion is you keep driving rods until you get 10 Ohms too. if the warranty is void because you don't drive the rods, it is equally as void if you don't meet the ten Ohms criteria as well.
iwire said:It was 10 ohms when I left, it must have degraded. :wink:
petersonra said:If you are only putting in the ground rods because the instructions say so, than my suggestion is you keep driving rods until you get 10 Ohms too. if the warranty is void because you don't drive the rods, it is equally as void if you don't meet the ten Ohms criteria as well.
My suggestion is drive one rod at each spot, tie it to the steel, and tie them all together with a #4 piece of copper wire underground. With all those rods, the wire, and the steel, if you don't make ten Ohms, it is just not meant to be.