Kinda the same question as why only 6 AWG to a ground rod, because lightning does not care what size it is........well as i believe roger said the attachment is not for personal safety and more so for Lightning ( and it does not care...), Transients and Line Surges so basically shoot for 25 or less and if not install a second.....90% of the installers would not buy the equipment needed to actually do the test properly and if they purchased a 3 point measuring device would probably test that incorrectly anyway....so simply add the second rod and be done and move on.......after all thats what we have helpers for.....;( oh dear....I steppin in that one.