Noticed something I need another view on in a commercial application Not my job, got rained out and just visiting a buddy when inspector showed up. 4 square metal boxes ran back to back. Have a chase nipple connecting in the center of the boxes with a lock ring on either side. On one side, there is a green ground wire attached to a green ground screw in the back of the box (typical). The other side has ?.nothing.
The MC is installed on the box without the ground wire. The inspector said it was fine, as the MC had a ground inside and they could pigtail from that in one side and feed it through to the other, using the chase nipple as the continuation of the ground.
I always thought 250.148 (C) meant you had to use the screw or a clip. Inspector says the chase nipple, the ground wire in the MC cable and/or the MC flex conduit satisfies the ?listed grounding device? requirement in this section.
Thoughts?
The MC is installed on the box without the ground wire. The inspector said it was fine, as the MC had a ground inside and they could pigtail from that in one side and feed it through to the other, using the chase nipple as the continuation of the ground.
I always thought 250.148 (C) meant you had to use the screw or a clip. Inspector says the chase nipple, the ground wire in the MC cable and/or the MC flex conduit satisfies the ?listed grounding device? requirement in this section.
Thoughts?