A contractor installs a new 400amp disconnect with 400amp fuses. Fed from the building 2000amp service. He taps on load side of 2000amp service switch and runs 2 pipes each has 4-350cu and a 2cu ground to new disconnect. Using the 25ft. tap rule 240.21(B)(2)
This is a feeder tap.
1. How is the correct way to size this ground for each pipe when using the tap rule?
2.Looks like 350cu THHN is to small to meet 240.21(B)(2) breaker lugs is 75 degree rated?