I have a ground system that is composed of 3 ground electrodes. I had a 3 point potential fall test performed on each one and know the resistance of each. I, however, need to know the ground resistance of the whole system not just of each individual one. I understand that the total system resistance will be less than the resistance of least resistive ground electrode, however, I need to make sure, based on a specification, that it is below 5 ohms.
Is there a way to measure the full ground electrode system without detaching a ground electrode and measuring each one individually? I have read about the "clamp on" measurement, this addresses the "not disconnecting" concern but it also goes on to say that it still only measures the individual ground electrode resistance.
I don't believe I can take the resistance values of each electrode and add them in parallel due to differences based on sphere of influence of each acting upon the other.