jutasi
Member
- Location
- Cincinnati, OH
Thanks. This will help me "sell" this idea to the folks who are NOT doing it correctly!!Pulled this from pg&e
Thanks. This will help me "sell" this idea to the folks who are NOT doing it correctly!!Pulled this from pg&e
no. As clearly labeled, this is the SOLAR ciruit (DC toAC inverter). conductors from line tap at right.Looking at pic I assumed the pipe out of the bottom was you line side tap. No egc in raceway
The rule in the 2020, found in 250.25(A) tells you that you treat the supply side disconnect just like a service disconnect.After reviewing 250.24(A) through (D) I see NOTHING that says the neutral should be tied to earth ground except at the main panel. Would you agree??
250.25(A) Grounded System.
If the utility supply system is grounded, the grounding of systems permitted to be connected on the supply side of the service disconnect and are installed in one or more separate enclosures from the service equipment enclosure shall comply with the requirements of 250.24(A) through (D).