installing smoke detectors in existing apartment buildings. using a plastic round cut in box. smokes do not have a ground wire. would it be required to terminate the ground wire from where it is fed from? such as a metal light j. box?
thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
All ground wires need to be terminated. 250.148. The one at the end of the line does not if there is no means to ground it- such as the smoke detector.

Why would you not terminated it. If someone wants to continue that feed from the SD then the ground would be available.
 