ground wire size
spencersct
New member
I am installing an 60amp three conductor sub-panel 700feet from main panel. Because of the distance I am using #1 feeder wires. How do I calculate the ground wire size?
ground wire
ground wire
You increase the kcmil of the required equipment ground by the same percentage that you increased the phase conductors.
(Compare the area of the #1's you are using to the required #6. Use that same percentage as a multiplier for the area of the required #10)
See chapter 9 table 8 to convert the #1 and #6 to circular mills. #6 is 26240 and #1 is 83690 so you have increased your wire size by about 3.2 times.