I've been confused about sizing the GEC/EGC in grid tied systems for some time now. My company has just defaulted to having a #8 ground (at least) everywhere in the system to cover our butts.
My question is concerned with Grid tied, Transformerless(ungrounded), rooftop mounted PV arrays, and specifically with the wire run from the inverter to the main panel. Let say for example the circuit requires #10 conductors and we are running romex. In the past we would have pulled an additional #8 ground with the romex from the inter to the panel. My suspicion is that this is unnecessary?
Will the #12 wire that is included with 10-3 romex be sufficient in this case and most importantly, meet code.
Thanks for your input in advance
I've been confused about sizing the GEC/EGC in grid tied systems for some time now. My company has just defaulted to having a #8 ground (at least) everywhere in the system to cover our butts.
My question is concerned with Grid tied, Transformerless(ungrounded), rooftop mounted PV arrays, and specifically with the wire run from the inverter to the main panel. Let say for example the circuit requires #10 conductors and we are running romex. In the past we would have pulled an additional #8 ground with the romex from the inter to the panel. My suspicion is that this is unnecessary?
Will the #12 wire that is included with 10-3 romex be sufficient in this case and most importantly, meet code.