What size ground wire would you run in the conduit with multiple circuits I want to run one ground wire?
Sent from my iPhone using Tapatalk
Sent from my iPhone using Tapatalk
What year code book do you have in front of you?What size ground wire would you run in the conduit with multiple circuits I want to run one ground wire?
Sent from my iPhone using Tapatalk
See 250.122(C) for your answer2017 pvc
Sent from my iPhone using Tapatalk
My largest breaker in that conduit is a 2 pole 30 feeding a heat pump so what size egc do I need in that Conduit if I only run one ground wire with multiple circuits ?
Sent from my iPhone using Tapatalk
#12
Sent from my iPhone using Tapatalk
What did the code article tell you?
#12
Sent from my iPhone using Tapatalk
Good answer
Rating or Setting of
Automatic Overcurrent
Device in Circuit Ahead
of Equipment, Conduit,
etc., Not Exceeding
(Amperes)
If his 30 amp breaker is feeding a heat pump it is possible the heat pump branch circuit conductors only need to be 12 AWG and if that is the case the EGC doesn't need to be any larger then the branch circuit conductors, which is also stated within 250.122 (in 2014 NEC, may have been a part of an exception at some point in earlier years)Since the table says this:
Anything over 20A exceeds the column for #12 so looks like you need a #10. I'm still on the 2008 and that's what is says to use. The table has changed some in the 2014 & 17 but says basically the same thing.
If his 30 amp breaker is feeding a heat pump it is possible the heat pump branch circuit conductors only need to be 12 AWG and if that is the case the EGC doesn't need to be any larger then the branch circuit conductors, which is also stated within 250.122 (in 2014 NEC, may have been a part of an exception at some point in earlier years)
He did mention the 2 pole 30 is for a heat pump. <---CLUEOP didn't mention MCA, he only said 30A breaker. So that's what my answer was based on.