I 'm pretty sure I am right about this , but I need some positive reinforcement.
We have a service on a pole, the service is grounded and the neutral is bonded.
The service serves to small buildings. the feeders running to these buildings are in PVC underground No ground wire was pulled from the service to these buildings. They are sub panels from the service. The panels themselves are grounded via #6 and a driven rod. A ground wire should have been pulled and sized as an equipment ground. Am I correct?
We have a service on a pole, the service is grounded and the neutral is bonded.
The service serves to small buildings. the feeders running to these buildings are in PVC underground No ground wire was pulled from the service to these buildings. They are sub panels from the service. The panels themselves are grounded via #6 and a driven rod. A ground wire should have been pulled and sized as an equipment ground. Am I correct?