can i run the ground wire from the rod into the meter socket instead of into the panel?
Rick, I have never seen any meter that does not have provisions for the GEC.Single gang meters usually does not have a spot to land this but mutiple meter sockets do.
Neither have I :happyno: Maybe an East coast West coast thing. I think that the termination has to be "accessable" and with a seal on the meter socket, maybe it be considered non accessable.Rick, I have never seen any meter that does not have provisions for the GEC.
Roger
That is the way it is done in NH 99% of the time.can i run the ground wire from the rod into the meter socket instead of into the panel?
I recently failed a City of San Jose inspection for this. Inspector said he was following PG&E's greenbook.
Tried fruitlessly to reason with him.
To my point in my post #3 re "can i run the ground wire from the rod into the meter socket instead of into the panel?
" So you run the EGC to the meter socket and then what do yo do with it? If there was a grounding lug does that mean that you have to run a separate EGC and neutral to your main load center from the meter?
And the other connectioms do not need to be accessible? Are locked electrical rooms accessible?The connection point must be accessible, the meter enclosure is locked by the POCO. Doesn't sound accessible to me.![]()
Along with Jap's point, how many times have any of us been out in the middle of the night to fix a loose GEC connection?
Roger
The inspector was correct.
From the Green Book:
Applicants must locate the terminations (e.g., ground bus) for their
grounding electrode conductors outside of any section that PG&E
seals.
It only has to be "accessible", not "readily accessible". I see the connection in the sealed meter enclosure as being accessible.Am I remiss in thinking that the aforementioned accessibility is a requirement?