Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
I almost never pull a green unless it's required.
So say you have 3/4" EMT from a receptacle up to a 4" box in the ceiling? You are only pulling H&N?
I almost never pull a green unless it's required.
Ok so what if spec doesn't ask for it but schedule shows it like in the attached pic. They can claim they require it based on panel schedule, no?
Yes, no EGC of the wire type, unless require by the project specifications.So say you have 3/4" EMT from a receptacle up to a 4" box in the ceiling? You are only pulling H&N?
Absolutely. I've wired complete buildings with EMT and used no EGCs except for pigtails where needed.So say you have 3/4" EMT from a receptacle up to a 4" box in the ceiling? You are only pulling H&N?
Yes, every time I get the chance. And don't even get me started on the 3/4" minimum conduit size. I'd like to find the guy that started that spec and pound him into the other side of the earth and take what's left and throw it in the middle of a two lane bridge at rush hour.So say you have 3/4" EMT from a receptacle up to a 4" box in the ceiling? You are only pulling H&N?
Don't get me started,,,, we haven't got to compression only fittings yet. I've got a bottle of nail polish remover and an exacto knife in mind for that guy.Don't t hold back Dave, say what you feel.
Roger
So say you have 3/4" EMT from a receptacle up to a 4" box in the ceiling? You are only pulling H&N?
Somewhat the same can be said for 1/2 EMT vs the 3/4 EMT.Yes. Why pull an extra conductor that no one is paying for and is not required. On a large project add up all of the additional EGC's and terminations and you will find a significant amount of cost. If that is not included in your bid you will be losing money.
Somewhat the same can be said for 1/2 EMT vs the 3/4 EMT.
If it is specified bid it that way. If you can save them $$ doing it another way, may need the designers blessing, or at very least inform owner it is an alternate design.
A 1" pipe for a cat6 cable is not overkill! That single cable will double or triple within months! And other cables will probably share that pipe-- phone, cable TV, etc.I agree, give them what they want unless they're asking for you to value engineer the job. I've seen so many dumb spec's over the years, 1" stub ups for a single CAT6 cable, no more than 3 CCC's in any raceway, EMT only even in the walls, #8 EGC's with #12 branch circuit conductors, the list is endless.
Over the years, I've appreciated that kind of foresight!A 1" pipe for a cat6 cable is not overkill! That single cable will double or triple within months! And other cables will probably share that pipe-- phone, cable TV, etc.
And you didn't have to break open the walls to do it!Over the years, I've appreciated that kind of foresight!
Our 40 year old building had 1" pipes to offices jammed with 25-pair phone cables, 25-conductor parallel printer cables, and twinax cable for the IBM terminals. All replaced with 2 or 3 CAT6, and a RG-6.
Sometimes it is sometimes maybe isn't. Stub from a slab, maybe a good idea to go large if any doubts. Stub from above a suspended ceiling, maybe not as worthwhile to go large.A 1" pipe for a cat6 cable is not overkill! That single cable will double or triple within months! And other cables will probably share that pipe-- phone, cable TV, etc.
How many times have we seen conduit, and connectors pulled apart.
Right on!That has certainly happened. However, say that happens, what are the chances that after that ALL the following happen?:
1. There is not another path back to the source somewhere
2. The conduit break is not repaired
3. A fault happens
4. Someone is injured or a fire occurs.
IMO there are many other things more important in an electrical system that no one seems to care about anymore because everyone is obsessed with grounding.
Also not sure why so many seem to think redundant bonding is so necessary, but no one seems to think redundant OCPD's and GFCI's are a good idea.