I am running 3 circuts through EMT conduit, do I need to run a ground wire for each of the three circuts in the same conduit, or is it ok to just run one???
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I am running 3 circuts through EMT conduit, do I need to run a ground wire for each of the three circuts in the same conduit, or is it ok to just run one???

You don't need a ground with emt but if you want one or specs call for it then size one to the largest circuit needed in the run.
 