Ground??
mstrlucky74
NJ
120/208V panel. RTU heat feeds show 3 phase(hots) and no neutral. Shouldn't a separate ground(EGC) be required? If not why? Thanks.
You can use the metal raceway as an EGC. If there is a flexible raceway involved and the equipment will move or vibrate then you must install a wire type EGC within the flexible raceway. I'm glad that you clarified the word "ground" by calling it the correct term, EGC. :)
Thanks. What code section is that regarding the EGC in the FMC? Thanks.
It’s likely listed in the project specs that all conduits have an appropriately sized EGC.
Usually the only place I see the ground size specified in a schedule is on panel feeders.
Yes it usually does but we always figure the conduit to be the EGC.
Sent from my SM-G955U using Tapatalk
On our current project we're doing the same thing, no wire type EGC's. Seems that the building owner wants code minimum to save money on the 2.3 billion dollar project.
I actually really love to hear that. Seems like hardly anyone uses the raceway as egc anymore.