enireh
Senior Member
- Location
- Canyon Lake,TX
if the home is serviced with plastic pipe for the water, then the ground rod and rebar in the slab is sufficient?
if there is no rebar in a slab is the ground rod sufficient? if the water pipe is plastic
Yes. We follow this method all the time.If by "ground" you mean grounding electrode then all that you need is the CEE if the rebar qualifies as an electrode (it must be in the footing). The ground rods are not required.
If there is no rebar you could run 20' of #4 in the footing and avoid the ground rods.
No different than when you use rebar. There is no connection if you leave the wire long enough to reach the meter or service panel. I never splice the Ufer.
That's how I would do it also unless the copper thieves get to it.
No different than when you use rebar. There is no connection if you leave the wire long enough to reach the meter or service panel. I never splice the Ufer.