ground
If by "ground" you mean grounding electrode then all that you need is the CEE if the rebar qualifies as an electrode (it must be in the footing). The ground rods are not required.
if there is no rebar in a slab is the ground rod sufficient? if the water pipe is plastic
Yes, if there is no CEE (meaning that there is no rebar in the footing or no footing) then you would need one ground rod at 25 ohms or less or two ground rods.
Yes. We follow this method all the time.
But don't forget to setup an intersysem bond. Without having an exposed wire run outside to the ground rods the Telcos wouldn't have anywhere to tie in their grounding wire.
Rob
Sent from my Pixel XL using Tapatalk
No different than when you use rebar. There is no connection if you leave the wire long enough to reach the meter or service panel. I never splice the Ufer.
That's how I would do it also unless the copper thieves get to it.
I was picturing you bringing it up out of the footer through the bottom plate or basement. Bringing it to the meter is way better.
Hmm, we do not bring the #4 ground to the meter base up here. Always the service entrance panel. Well, at least I have never seen it....;)
Burying it under the slab before the slab is poured will keep it from being stolen for sure, but difficult to connect to panel later.:D