chris kennedy said:08 "Ground" The earth
So what size Earth should be used? :wink:
chris kennedy said:08 "Ground" The earth
Parache said:know i got it 800amp= 700mcm 700mcm=#2/0 ground
thanks guys
Parache said:know i got it 800amp= 700mcm 700mcm=#2/0 ground
thanks guys
Parache said:got it! over 1100 mcm =3/0 ground
If you need access to the code check the links out belowrayrmelc said:Table 250.122
Need code book
Check your PM's.rayrmelc said:Table 250.122
Need code book
The Iceman said:I have a quick reference guide for copper wire size and conduit fill. I understand how to use the code book for this but when I looked at my chart under 800A it calls for 2 sets of 3-500KCM and 1-1/0 ground. Am I missing something about sizing parrallel conductors or is this chart wrong?
infinity said:That all depends on what your sizing. For an 800 amp feeder it may be correct. For the secondary conductors on a transformer to an 800 OCPD it's incorrect.
The Iceman said:Lets say its for an 800 amp feeder. Using table 310.16 the 75 degree column parralleling 500kcm only gives you 760 amps. And using table 250.66 the 1-1/0 ground would be wrong as well.
The Iceman said:I have a quick reference guide for copper wire size and conduit fill. I understand how to use the code book for this but when I looked at my chart under 800A it calls for 2 sets of 3-500KCM and 1-1/0 ground. Am I missing something about sizing parrallel conductors or is this chart wrong?
infinity said:If the connected load is 760 amps or less then you are permitted to go up to the next standard sized OCPD which is 800 amps. According to 250.122, the #1/0 EGC would be fine and is required in both of the parallel raceways.
The Iceman said:I forgot the next size up rule. Whats the article number thats under I need to review it.