We just had a thread on more or less the same thing.
The NEC requires one neutral per terminal. It does not prohibit two EGCs per terminal, but the listing/panel label has to allow that. Panel labels these days usually say it's only allowed for EGCs, if they say it.
Could a panelboard theoretically exist that is formally listed and labeled otherwise for two neutral (grounded) conductors under the same screw? And would this article of the NEC override using it that way?