I'm a journeyman in OKC and have recently gone to work for a contractor who derives a great deal of his business from the city and state. Most of what we do consists of highway lighting and traffic controls.
I have hit an empass with my employer. The state requires us to pull a hot (black) and neutral (white) to feed underpass lighting. Same is fed through underground pvc conduit which goes to rigid above ground and quite often seal tight is used to turn 90's.
The problem is that the city and state have exempted themselves from NEC jurisdiction. Accordingly, my employer disregards my complaints concerning safety.
The problems are as follows:
1) due to bid requirements, no equip ground is pulled with conductors.
2) the pipe is isolated from ground due to pvc underground.
3) the grounded conductor is bonded to each fixture and used as both the grounding and grounded conductor.
4) the light fixture is grounded on one leg and fed with 480 on the other. Though there is nothing, of which I am aware, preventing this...
the wire colors used give no forwarning of the voltage to be encountered.
I have found many references in code which under normal circumstances would outlaw most of the above. However, due to the fact that the state exempts itself from nec jurisdiction, there appears to be nothing I can do about it.
In short, I am afraid that someone could easily be hurt if not killed by such poorly engineered electrical work.
I am looking for ammo to take with me on my next visit to my employers office. I would like to see this all be changed to better safeguard the lives of the individuals who will work on it...who happen to be non-licensed and inexperienced at electrical work (also due to the exemption stated above).
I was hired to do industrial work on plants,airports and the like and have only come to find this all out during a lull in the work I normally do. It truly scares me.
What are your thoughts?
I have hit an empass with my employer. The state requires us to pull a hot (black) and neutral (white) to feed underpass lighting. Same is fed through underground pvc conduit which goes to rigid above ground and quite often seal tight is used to turn 90's.
The problem is that the city and state have exempted themselves from NEC jurisdiction. Accordingly, my employer disregards my complaints concerning safety.
The problems are as follows:
1) due to bid requirements, no equip ground is pulled with conductors.
2) the pipe is isolated from ground due to pvc underground.
3) the grounded conductor is bonded to each fixture and used as both the grounding and grounded conductor.
4) the light fixture is grounded on one leg and fed with 480 on the other. Though there is nothing, of which I am aware, preventing this...
the wire colors used give no forwarning of the voltage to be encountered.
I have found many references in code which under normal circumstances would outlaw most of the above. However, due to the fact that the state exempts itself from nec jurisdiction, there appears to be nothing I can do about it.
In short, I am afraid that someone could easily be hurt if not killed by such poorly engineered electrical work.
I am looking for ammo to take with me on my next visit to my employers office. I would like to see this all be changed to better safeguard the lives of the individuals who will work on it...who happen to be non-licensed and inexperienced at electrical work (also due to the exemption stated above).
I was hired to do industrial work on plants,airports and the like and have only come to find this all out during a lull in the work I normally do. It truly scares me.
What are your thoughts?