what 2011 code art. please i can not find it Thank you ?No, if the raceway contains service conductors the raceway is only required to be bonded on one end.
No, if the raceway contains service conductors the raceway is only required to be bonded on one end.
There is no specific "how to" in the NEC. 250.92 requires bonding of service raceways and 250.92(B) lists methods. Bonding one end of a raceway effectively bonds the raceway. A ground bushing is one acceptable method.what 2011 code art. please i can not find it Thank you ?