grounded bushings

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
2011 code must i use two grounded bushings. on meter base to panel back to back through 10" block wall ?
 
No, if the raceway contains service conductors the raceway is only required to be bonded on one end.
 
what 2011 code art. please i can not find it Thank you ?
There is no specific "how to" in the NEC. 250.92 requires bonding of service raceways and 250.92(B) lists methods. Bonding one end of a raceway effectively bonds the raceway. A ground bushing is one acceptable method.
 