On the system in question there will be a 480 delta to 240 delta transformer (with one center-tapped winding). Naturally, there are 230 VAC 3 phase loads on the secondary side and a few 230 VAC single phase loads spread around the two windings that are not center tapped (phases A to B and B to C).
If my jargon is correct these loads include the "bastard leg" (phase B in this case) which should be marked as orange since it is the highest voltage above ground.
That leaves the final secondary winding (C to A) which includes the center tapped winding which is also grounded via the ground rod. All of the 115 VAC loads are attached here (phase A or C to ground) and maybe even some 230 single phase loads (C to A) as needed to "balance" out the overall loading. (I also realize the 115 VAC loads are practically limited to about 30% of the transformer rating to keep the unbalanced loading from overheating the transformer; that part I think I understand)
That leaves my stupid question(s) . . . Why is it OK to ground this center tap when it is not really the theoretical neutral point (which should really exist at the center of all three "delta" phases)? Are there practical limitations on this set up? For example it is only ok for transformers up to a certain size, or is it always OK and the unbalanced currents just flow through the earth? Hope this all makes some sense and someone can explain it to me! Thank you. -- HD
If my jargon is correct these loads include the "bastard leg" (phase B in this case) which should be marked as orange since it is the highest voltage above ground.
That leaves the final secondary winding (C to A) which includes the center tapped winding which is also grounded via the ground rod. All of the 115 VAC loads are attached here (phase A or C to ground) and maybe even some 230 single phase loads (C to A) as needed to "balance" out the overall loading. (I also realize the 115 VAC loads are practically limited to about 30% of the transformer rating to keep the unbalanced loading from overheating the transformer; that part I think I understand)
That leaves my stupid question(s) . . . Why is it OK to ground this center tap when it is not really the theoretical neutral point (which should really exist at the center of all three "delta" phases)? Are there practical limitations on this set up? For example it is only ok for transformers up to a certain size, or is it always OK and the unbalanced currents just flow through the earth? Hope this all makes some sense and someone can explain it to me! Thank you. -- HD