R rhombus65 Member Mar 29, 2006 #1 I am trying to find the code reference that says that each grounded conductor must be terminated one per screw at a service. If anyone could point me in the right direction It will be appreciated.
I am trying to find the code reference that says that each grounded conductor must be terminated one per screw at a service. If anyone could point me in the right direction It will be appreciated.
R rhombus65 Member Mar 29, 2006 #3 rcarroll: Thank you for your reply. Is this requirement new in the 2005 cycle?
rcarroll Senior Member Location Fort Collins, Colorado Mar 29, 2006 #4 I can find it in the '02 code but not the '99
bdarnell Senior Member Location Indianapolis, IN Occupation Retired Engineer Mar 29, 2006 #6 I think 408.21 was new to the '02 book.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Mar 29, 2006 #7 While the rule was new in the NEC for 2002, it has been a part of the listing and instructions for the panel for many years. It was added to the code, because too many installers weren't following the instructions. Don
While the rule was new in the NEC for 2002, it has been a part of the listing and instructions for the panel for many years. It was added to the code, because too many installers weren't following the instructions. Don