Non-utility application with a -48V DC plant to serve computer equipment, which means we need to comply with the NEC. -48V means the positive terminal is intentionally grounded.
I am planning to have the grounded conductor identified as white or gray as required by 200.6
Anyone see a way around the 200.6 color code for the grounded conductor?
I thought maybe because it was 48V, it might be exempt, but the scope for Article 200 (200.1) seems to still require compliance for this application. I would say this is part of the premises wiring identified in the scope.
I am planning to have the grounded conductor identified as white or gray as required by 200.6
Anyone see a way around the 200.6 color code for the grounded conductor?
I thought maybe because it was 48V, it might be exempt, but the scope for Article 200 (200.1) seems to still require compliance for this application. I would say this is part of the premises wiring identified in the scope.