Have not looked at the 2011 NEC yet... If you ran power to the light fixture, then dropped down to a light switch. What is the purpose of the grounded conductor requirement at the switch box and what would you do with it besides just cap it off?? Sounds a little strange to me.
Does an attic above this switch meet the intent of the exception?
so how would you run a switchloop then you would have to run a 3 wire assemble to the sitchbox after you hit the lightbox
In my opinion if you have to drill through the top or bottom plate of the wall, then you do not meet the requirements of the exception.
The issue is that UL has permitted the manufacturers of electronic switches to use the EGC as a grounded conductor. They permit each switch to put up to 0.5 mA of current on the EGC. The code does not permit the EGC to be used as the grounded conductor. UL said that they would revise their standard to prohibit using the EGC as the grounded conductor for these electronic switches only if the NEC was revised to require a grounded conductor at each switch box.
In my opinion if you have to drill through the top or bottom plate of the wall, then you do not meet the requirements of the exception.
But it does say ceiling that is unfinished on one side. For what it's worth a Mike Holt graphic depicts attic access as meeting the exception in his 2011 code change book.
This only applies if and when your locality officially adopts the '11 NEC.coworker told me today that the nec wants grounded conductors in switch boxes now.does anyone know about this .