Re: Grounded Conductor Problems
I just had another thought.
There will be currents on the service entrance neutral and GEC that will be produced on the PoCo distribution grid. This current will be in addition to the dwelling load unbalance current splitting at the MBJ between the GEC and the SE Neutral.
Setting a fixed trip level, in my opinion, will result in false trips or no trips at all, unless the GEC current stays in a narrow range.
The amount of load running at any one instant will determine the amount of current on the GEC. . .so I don't think there is a way to build a trigger based on the measurement of the amount of current on the GEC alone.
I think the GEC current has to be compared with the SE Neutral current. If the ratio of the two currents (or maybe the sum or the difference) changes abruptly and remains changed, then that change is the indicator of the neutral loss.