An office building service has a total computed load of 200 amps for each
ungrounded conductor and 60 amps for the grounded conductor.Equipment
terminations are 75 C , type THW copper.What is the minimal size for the
grounded conductor?
(A) 6 AWG
(B) 4 AWG
(C) 2/0 AWG
(D) 3/0 AWG
I get 4 AWG.