- Chapel Hill, NC
- Retired Electrical Contractor
240.4 applies to all conductors, including the grounded conductor. The real issue is if the code permits the use of a common grounded conductor outside of the two specific permissions in Articles 215 and 225. It is my opinion that there is no code rule that prohibits the use of common grounded conductors for other applications, but the code making panel does not agree.
Yeah, but we use a common grounded conductor to every sub panel without having to size the conductor on every OCPD so I am not sure why the code panel has a problem with this if the grounded conductor is sized appropriately.
Now if we had to size the ocp according to the rules from the handbook would we every have to size the grounded conductor larger than the feeder?