Several Residential PV installations have been going into our City for the past 4 years. I am the plan check engineer who checks each of these plans prior to permitting. I happened to go out in the field with the Supervising Inspector and one of the regular inspectors and discovered something that I had to comment on. PV systems with a grounded conductor have been installed using a white insulation for the grounded conductor (DC side). When entering the combiner/DC disconnect section of standard inverters, this puts the AC conductors in the same enclosure with the DC conductors. According to the 2010 California Electrical Code (based on the 2008 NEC), Article 200.6(D), "Where grounded conductors of different systems are installed in the same raceway, cable, box, auxiliary gutter, or other type of enclosure, each grounded conductor shall be identified by system."
I immediately instructed the installer and the inspectors that, at least at this point in the system, the grounded conductors of each system (DC and AC) shall be distinguished in accordance with CEC 200.6(D)(1) thru (3). This can be a special challenge on a commercial installation where there are multiple voltages present (120/208 and 277/480 are most common). When you throw a PV system into the mix, you may need to go to the third option in 200.7(A)(2): "A conductor with three continuous white stripes on other than green insulation."
I know that this has not been checked or corrected in ANY of the PV systems that were installed before this issue came up. The transformerless inverter systems are ungrounded systems, so this is not an issue, as long as the insulation is a color other than white, gray, or green. We have not had issues with these systems, only the transfomer-type inverter systems.
Of course, this is NOT an issue with micro-inverters or AC modules, as ALL of the installed wiring will be AC.
Since this came up here, I imagine this may come up elsewhere.
Just thought I would drop this on the forum to see what turns up.
Wayne
In Magic Mountain Land
I immediately instructed the installer and the inspectors that, at least at this point in the system, the grounded conductors of each system (DC and AC) shall be distinguished in accordance with CEC 200.6(D)(1) thru (3). This can be a special challenge on a commercial installation where there are multiple voltages present (120/208 and 277/480 are most common). When you throw a PV system into the mix, you may need to go to the third option in 200.7(A)(2): "A conductor with three continuous white stripes on other than green insulation."
I know that this has not been checked or corrected in ANY of the PV systems that were installed before this issue came up. The transformerless inverter systems are ungrounded systems, so this is not an issue, as long as the insulation is a color other than white, gray, or green. We have not had issues with these systems, only the transfomer-type inverter systems.
Of course, this is NOT an issue with micro-inverters or AC modules, as ALL of the installed wiring will be AC.
Since this came up here, I imagine this may come up elsewhere.
Just thought I would drop this on the forum to see what turns up.
Wayne
In Magic Mountain Land