My question might seem a bit silly but since I'm based in Europe, I'm not fully familiar with American standards. Is it allowed to disconnect the grounded (neutral) conductor in a UL508A control panel that will be used to operate an industrial machine (NFPA 79)? I'm working on a 480Y/277V network.
In the UL508A standard, I found the two following points, which require disconnection of the ungrounded conductors but, in my opinion, do not explicitly prohibit disconnection of the neutral:
I would like use 4P or 3P+N circuit breaker or disconnecting means.
Thank you very much for your replies!
In the UL508A standard, I found the two following points, which require disconnection of the ungrounded conductors but, in my opinion, do not explicitly prohibit disconnection of the neutral:
- 31.2.1 A branch circuit protective device shall be installed in each ungrounded conductor to the load(s) involved.
- 30.3.2 The disconnecting means shall open each ungrounded conductor of the supply circuit.
I would like use 4P or 3P+N circuit breaker or disconnecting means.
Thank you very much for your replies!