The saga continues... Alright, so here's where we're at:
It turns out that the calculated load for the new panelboard is approximately 325Amps, 208Y/120V. This panel is actually served with #300AL & #250AL neutral w/ #1 AL EGC.
The feeders were originally upsized due to voltage drop concerns as the load was closer to 400 Amps. However, the original installation was done in 1974, and they failed to upsize the EGC. My first code book dates to 1987, and at that time it was required to upsize the EGC per NEC 250.122(B) (2008 NEC then 250.95) proportionately with the phase conductors. My question is this, now that our load would adequately be served with 325Amps, and knowing that we would not have to upsize the feeders due to voltage drop, is the #1 AL EGC adequate despite the fact that the 250.122(B) would require that we upsize EGC regardless? What if I fuse the main at the switchboard feeding this new panelboard at 350Amps, what's the opinion? Would it be acceptable to leave the #1AL EGC rather than installing a new #1/0 (which would be proportionately increased)?
It's been a battle dealing with an owner who doesn't want to spend $ and keeps requesting that we find a way to make it work. The alternative isn't easy, but if it has to be done than he'll have no choice. I wanted to ask the AHJ for thoughts, but the owner sees that as a last resort.
Thanks to all.
It turns out that the calculated load for the new panelboard is approximately 325Amps, 208Y/120V. This panel is actually served with #300AL & #250AL neutral w/ #1 AL EGC.
The feeders were originally upsized due to voltage drop concerns as the load was closer to 400 Amps. However, the original installation was done in 1974, and they failed to upsize the EGC. My first code book dates to 1987, and at that time it was required to upsize the EGC per NEC 250.122(B) (2008 NEC then 250.95) proportionately with the phase conductors. My question is this, now that our load would adequately be served with 325Amps, and knowing that we would not have to upsize the feeders due to voltage drop, is the #1 AL EGC adequate despite the fact that the 250.122(B) would require that we upsize EGC regardless? What if I fuse the main at the switchboard feeding this new panelboard at 350Amps, what's the opinion? Would it be acceptable to leave the #1AL EGC rather than installing a new #1/0 (which would be proportionately increased)?
It's been a battle dealing with an owner who doesn't want to spend $ and keeps requesting that we find a way to make it work. The alternative isn't easy, but if it has to be done than he'll have no choice. I wanted to ask the AHJ for thoughts, but the owner sees that as a last resort.
Thanks to all.