brian john
- Kilmarnock, Va
- Retired after 52 years in the trade.
We have been working a job for 2 years with a grounded neutral issue. High current tripping the GFP at the 200 amp setting (where we found the gfp set). We could not get a long enough outages to isolate the problem and had to do the job in bits and pieces, worked on it again tonight (my guys are still there I left after isolating the major issue.)
Based on the high level of ground current I figured it had to be in the busway as branch circuits seldom contribute this high a level of ground current. This portion of the job had me worried for weeks as we had to take horizontal and vertical busway apart to isolate the sections.
We did locate over 100 branch circuits 6 months ago with grounded neutrals and are in the process of clearing these.
We also found the busway neutral shorted to ground this was also located 6 months ago.
What we found was when the busway was assembled the ground bus 1/8 copper was pinned against the neutral bus under the busway coupling insulator. Of course we did not locate this right away it was in the last coupling we took apart.