What is the main purpose of the three wire 120v circuit with 3 prong grounded receptacles compared to the older 2 wire 2 prong receptacles? Human safety, lightning protection, etc.?

Thank you.
 
What is the main purpose of the three wire 120v circuit with 3 prong grounded receptacles compared to the older 2 wire 2 prong receptacles? Human safety, lightning protection, etc.?

Thank you.
Human safety.

The metal body or frame of devices plugged into the outlet would be connected to the "grounding" wire. If a fault occurred which allowed the metal body or frame to become energized, the current would flow back to "ground" and the resulting short-circuit would cause the OCPD (breaker or fuse) to trip/blow.

If not for the ground wire, the metal body or frame of the faulty device could remain energized creating an electrocution hazard.
 
190626-9842 EDT

If there was a solid short circuit in the motor from hot to the motor frame, then for most branch circuit wiring the voltage motor frame voltage would be about 1/2 the supply voltage relative to remote earth. And local earth voltage at the motor might be about equal to remote earth.

Note: the branch circuit EGC gets its connection to earth back at its main panel or thereabouts.

.
 
190626-9842 EDT

If there was a solid short circuit in the motor from hot to the motor frame, then for most branch circuit wiring the voltage motor frame voltage would be about 1/2 the supply voltage relative to remote earth. And local earth voltage at the motor might be about equal to remote earth.

Note: the branch circuit EGC gets its connection to earth back at its main panel or thereabouts.

.

Yup, and this is where the breaker comes in, killing that 60 volts to remote earth.
 