crossman
Senior Member
- Location
- Southeast Texas
I would like to see a diagram of the service/inverter/isolation xfmrs just for my own knowledge. Any chance of that?
ramsy said:But, crossman since my apprenticeship was canceled by NECA, my "Handyman, will work for food" signs are waring out.
Smart $ said:Does anyone have an actual "process" and connection diagram?
From what I am gathering from the manufacturer's online literature, the 3-phase inverter is delta connected to a wye system... in which case I can see why RichardM is calling it an ungrounded wye.
Smart $ said:Does anyone have an actual "process" and connection diagram?
From what I am gathering from the manufacturer's online literature, the 3-phase inverter is delta connected to a wye system... in which case I can see why RichardM is calling it an ungrounded wye. The literature available online is very vague.
...but this just takes us back to the requirement for system grounding. In this case, I believe you must initially go to 705.50. And even though there is an exception thereof, the system under exception is grounded. For a not exceptionable system, we are referred back to 250.20 Alternating-Current Systems to Be Grounded noted earlier. The system must meet the requirements therein.RichardM said:Even though I didn't get a chance to ask specifically if the inverter is giving me a delta or wye, Xantrex personnel repeatedly mentioned the connection as being an ungrounded wye. They stated that the reason neutral comes to neutral, and is not grounded, is their interpretation of the IEEE standards to measure line to neutral voltages.
Apparently the neutral may also be fairly undersized due to the way it is setup.