MannyBurgos
Senior Member
- Location
- Waukegan, IL
Yes you can terminate your GEC (or GEC tap) to the neutral busbar. You can also terminate it at the EGC busbar if there is an appropriately sized wire-type main bonding jumper between neutral and EGC busbars. However, you are permitted to terminate a GEC to and at any point along the grounded [neutral] service entrance conductor. A GEC is only required to be connected within the same enclosure as a system bonding jumper of a separately derived system... not a service.
250.64(C)(2) says sections of busbar. It does not say sections of busbar and wire, nor does it say anything about listed grounding connectors that are not irreversible.
It says sections of busbars are peemitted to be CONNECTED together to form a gec. Connection of a neutral and ground busbars are often connected via a wire... Ground bars are listed for the purpose as well as are neutral lug kits. Listed would mean that if the wire size is 4awg, the termination better be liated to accept that wire size for example; the neutral lug kit.