Hello,
Will I need to run a egc 1/0 aluminum from the ct can neutral to the metal rack that holds the service gear. This is an out side service with 3-200 amp disconnects feeding 3 panels. The rack is two 6" rigid pipes (10') long with 3 ft in the ground with concrete and unistrut bolted between them. The strut is what the service gear sit on. I plan to wire #6 copper from the 3 disconnects to the ground rods. I was wondering if I need to run a 1/0 aluminum wire from the ct can neutral to the steel posts. Not sure if that will work, but it is feed by parallel 500 mcm Aluminum. It wont be accessible in the ct can.
Will I need to run a egc 1/0 aluminum from the ct can neutral to the metal rack that holds the service gear. This is an out side service with 3-200 amp disconnects feeding 3 panels. The rack is two 6" rigid pipes (10') long with 3 ft in the ground with concrete and unistrut bolted between them. The strut is what the service gear sit on. I plan to wire #6 copper from the 3 disconnects to the ground rods. I was wondering if I need to run a 1/0 aluminum wire from the ct can neutral to the steel posts. Not sure if that will work, but it is feed by parallel 500 mcm Aluminum. It wont be accessible in the ct can.