I am always in a quandry when rewiring an existing building as to how to ground it. I believe that wimpy ground rods are fine for a small residence, but inadequate for a commercial building of any size - I'd rather see a Ufer ground than anything else, failing that a nice ground ring at the footing. We have two projects right now where we are doing major remodels on existing buildings.
Building A is a historic theatre built in the 1920's, when "grounding" meant your Model A was high centered on the road ruts. We are putting a new 1200A 208V service in. I'd love to clamp onto some rebar for a Ufer ground, but there isn't much new concrete available. It's all brick, there is almost no building steel. There is a little bit of steam piping, and some new water pipe no doubt connected to a plastic pipe out in the street. The building covers a city block, and I'd love to put in a ground ring around the whole thing, except we'd have to dig up a quarter mile of sidewalks to do it. I hear horror stories about big buildings grounded with a skinny ground rod at one corner, where the other corner is 50V to "ground" due to stray current.
Building B is worse - it is a physical plant for a hospital complex. There are a total of 6 service entrances. I go back through plans to the '60's, and find that grounding is not addressed. I do find ground buses in some of the switchgear, but nothing on old plans indicating a ground ring, Ufer ground, ground rods, and so on. I doubt there is anything there at all. I also doubt that the various service entrances are tied together - unless some conduit happens to go from frame to frame, the switchgear grounds are probably floating. So far tracing down ground conductors has resulted in no conclusions.
I run into this constantly - we are asked to put a new service into an existing building, where the existing ground system is either nonexistent or inadequate. What approaches have people used in the past? Do you really dig up all the sidewalks for a ground ring? Do you start jackhammering concrete until you can expose some rebar? Do you drive ground rods at four corners of the building and hope for the best?
Building A is a historic theatre built in the 1920's, when "grounding" meant your Model A was high centered on the road ruts. We are putting a new 1200A 208V service in. I'd love to clamp onto some rebar for a Ufer ground, but there isn't much new concrete available. It's all brick, there is almost no building steel. There is a little bit of steam piping, and some new water pipe no doubt connected to a plastic pipe out in the street. The building covers a city block, and I'd love to put in a ground ring around the whole thing, except we'd have to dig up a quarter mile of sidewalks to do it. I hear horror stories about big buildings grounded with a skinny ground rod at one corner, where the other corner is 50V to "ground" due to stray current.
Building B is worse - it is a physical plant for a hospital complex. There are a total of 6 service entrances. I go back through plans to the '60's, and find that grounding is not addressed. I do find ground buses in some of the switchgear, but nothing on old plans indicating a ground ring, Ufer ground, ground rods, and so on. I doubt there is anything there at all. I also doubt that the various service entrances are tied together - unless some conduit happens to go from frame to frame, the switchgear grounds are probably floating. So far tracing down ground conductors has resulted in no conclusions.
I run into this constantly - we are asked to put a new service into an existing building, where the existing ground system is either nonexistent or inadequate. What approaches have people used in the past? Do you really dig up all the sidewalks for a ground ring? Do you start jackhammering concrete until you can expose some rebar? Do you drive ground rods at four corners of the building and hope for the best?