Grounding a big existing building
dereckbc said:
I suspected you had 4160, that is why I danced around it.
As for the GES I have more questions than answers. Without seeing and being familiar it is hard to answer. Is the new service part of new construction? If so I would probable use a "Star Point" counterpoise under the the transformer pad. From there try to figure out how to bond to the other GES systems already in service either via sub-terrain or above ground.
Sorry not much of an answer on the GES part, need more info, lot more info.
Obviously you'd need to know a lot more and I don't expect you could do more than suggest some guildelines. The building is existing. No new concrete footings are planned so we don't get a CEE. I have reviewed plans back to the 1960's and grounding (and bonding!) is not addressed.
Another guy is inspecting the bonding (but not the earthing) in the building, and soon it will all be tied together nicely. He finds bonding violations every time he looks for them. None of the small distribution transformer SDSs are properly bonded. Oh yeah, and there are generators - several now and more planned soon. Not little ones either and nobody can tell us how they are bonded/grounded. All the power transformers are on the roof. I know that some of the delta connected services wander around, one leg being higher voltage than the others, which makes me wonder if they are tied to ground at all. In 4160V, you begin to worry about overvoltages if the service can wander around because it is not properly grounded. You also begin to worry that a phase to ground fault might not be detected!
Your point about subbing the lightning protection review to a master label firm is well taken. I'll go down that path instead of trying to do it myself. I've done plenty of lightning protection but not a system this complex.
You can see why I might be nervous about grounding existing buildings given the medium voltage and planned generators. This isn't the only existing building I am working on but it is the most complex.
Dont' know the exact soil resistivity, but it is in a loamy area near the gulf coast, which remains wet all the time and presumably was swamp before it was built upon. Soil resistivity and moisture should be very adequate. Would you go so far as to measure soil resistivity?
Very little steel structure except in the roof, most of the building is masonry or concrete walls and concrete columns. So there is not much there to tie into, nor to bond to. So far we have been running EGC's back to the service equipment for any SDS's such as transformers.
I could ask that they get out a chipping hammer and expose some rebar to bond to down in the lowest basement. I am tempted to do that to make sure I get a lot of sleep at night. There is also an old abandoned service entrance in a pit in the basement - I haven't inspected it to see if they left some handy grounding points there. It is very, very likely that when that service was moved, the new service was NOT earthed at all. The size of that service, the existing bonding violations, and the medium voltage makes me nervous about this.
So I am trying to establish some general guidelines to follow for this kind of job. For example, a target ground resistance.