I am stationed overseas right now, no code book handy!! My friend and I were talking about his cabin we are going to wire when we get back, about getting power from a portable 5500W generator. He is going to bolt the gen down and permanantly wire it to the cabin. I was discussing the grounding with him, stating that the gen be considered the "main service" , and the cabin be an outbuilding. without having a book to refer to some of the questions I have, I was just trying to come up with the right solutions for the wiring from the gen to the cabin (not carrying the ground and pounding rods vs. not) and the grounding on the gen and the cabin? Thanks for time !!
I can tell you what I did. Quien Sabe? It may even be right.
I've got a 3.3kw gen, batteries and a 3kw inverter/30A charger. The gen is quiet and has a BIG muffler. I pulled the wheels, set on blocks to provide access for oil drain. And I put it in its own house about 70' away. I can still hear it, but it is pretty, uhhh, muffled :roll:
First off, forget you have a service - because you don't. The portable 5.5kw gen will have a 30A CB and a 30A, 240V, 4w receptacle (high probability). The feed from the gen to the gen house panel is a feeder, not a service. The feed from the gen to the cabin is a feeder not a service.
In my case:
Removed the NG bond from the gen,
Ran 4W, 240 from the gen 30A receptacle to a small (2 ckt) MLO panel in the gen house. Lights, vent fan, one receptacle. No bond in the gen house panel. Ground rod at the gen house GEC connected to genhouse panel ground bar.
Ran 4w from the genhouse panel to the cabin panel (actually to the inverter - then 4w from the inverter output to the panel. The inverter just passes through - relay- when the gen is on)
NG bond is in the cabin panel. Ground rod at the cabin panel.
I'm clear north, so there were a few other issues - but not related to your OP.
You have a computer. You can get access to an NEC code