250.86 OtherConductor Enclosures and Raceways. Except
as permitted by 250.112(I), metalenclosures and raceways
for other than service conductorsshall be connected
to the equipment groundingconductor.
Exception No. 1:Metal enclosures and raceways for conductors
added toexisting installations of open wire, knoband-
tube wiring, andnonmetallic-sheathed cable shall not
be required tobe connected to the equipment grounding
conductor wherethese enclosures or wiring methods comply
with (1) through(4) as follows:
(1) Do notprovide an equipment ground
(2) Are in runsof less than 7.5 m (25 ft)
(3) Are freefrom probable contact with ground, grounded
metal, metallath, or other conductive material
(4) Are guardedagainst contact by persons
Exception No. 2:Short sections of metal enclosures or
raceways used toprovide support or protection of cable
assemblies fromphysical damage shall not be required to
be connected tothe equipment grounding conductor.
Exception No. 3:A metal elbow shall not be required to be
connected to theequipment grounding conductor where it
is installed ina run of nonmetallic raceway and is isolated
from possiblecontact by a minimum cover of 450 mm
(18 in.) to anypart of the elbow or is encased in not less
than 50 mm (2 in.) ofconcrete.