1 I don't know why we indulge you on this forum when you don't know this really basic stuff. :roll:
2 Overcurrent devices are not allowed in grounded conductors (neutral, in this case), or in EGCs.
3 Probably not. Most engineers design feeders for a 2% maximum voltage drop. The inverter can handle plus 10% or minus 12%, so a much bigger window.
Note that by reducing the current that's fed from the grid, the inverter at max output reduces the voltage drop on the sub feeder. So your scenario is not worst case. Worst cases would be:
a) a constant full load on the subfeeder causes voltage to drop below the inverters window in the morning, before the inverter turns on. Inverter never sees a good voltage and never turns on.
b) zero load at the subpanel, full PV output, too much voltage rise from service to inverter.
Any load that turns on after the inverter turns on mitigates the situation.
So really your obligation is to calculate drop/rise from the service point, and make sure it's about 2% or less.
4 FWIW, we always roll with minimum #10 wire for inverter output, even if it's 20A or less.
1 It's gotta be either my outside of the box thinking, or my ability to translate zman's questions. Or possibly that I do make good points every now and then (quoting you
2 Right. I'm still a little confused by the JAZ's diagram and the EGC/GEC issue. You told him his 1st diagram was cool, and then he deleted the GEC, so...?
In both diagrams he posted, the N and G and bonded at the main panel and not bonded at the secondary panel.
Looking at the second one, the N from the grid is connected to the N bar in the main panel at the same spot as the N wire which goes to the N bar in the secondary panel and the N from the inverter is connected to the opposite end of the sec. panel N bar.
That N line from the grid is also connected to the G bar in the main panel. (Bonded, right?)
So...why is the N from the inverter connected to the secondary panel at all?
If the N from the inverter ran to the N bar of the main panel, wouldn't that satisfy what the POCO is asking for, because the EGC for the inverter would then "terminate" at the main panel?
Please don't get aggravated- just questions here.
I'm not saying JAZ should do this- just hypothetical- why not "terminate" the inverter EGC at the switch in JAZ's drawing?
This is the closest example I can find- yes, I know it's off-grid, but...
http://solar.smps.us/solar-system-diagram-offgrid.jpg
If the G from the inverter went to actual earth at the PV disconnect switch, then the N could pass through the switch, and N and G from PV Inverter bonded at the main panel?
3 Ok- so...a 120V of grid is supplying the loads in the AM. 2% drop is 117.V 12% drop from 120V is 105.6V, JAZ pointed out that: "A/C range on SMA TL-22 Series is 211-264 when operating at 240 volts. very wide range. "
211V at 240V is 105.5V at 120V.
So no problem with your a) scenario, but what about what I mentioned about a bunch of motors turning on while the PV is running at max output and the voltage dropping below 105.6V for a short time, therefore kicking the PV off?
4 Back to that SMA typo- assuming the 12-6AWG for L1, L2 and N outputs thing is NOT a typo- I'm correct that you can't use 4AWG for the L1 L2 and N, because of the physical structure of the inverter output (simply, they aren't lugs?)
Hey, great drawing btw if I didn't say that already. One thing-isn't the N wire going from the secondary panel to the main panel supposed to "jump" (as in not be connected to) the 2 100A breaker wires?
If you don't mind me asking, did yo use SmartDraw software to do the drawing?
1. ...And there is normally never any overcurrent device in the grounded conductor and absolutely never in the EGC.
Well..ok...but if the PV inverter's N and G are terminating at the secondary panel (where the 40A breaker is)...that doesn't make it a separate EGC system from the main panel EGC?
Like Jben said, if the N and G are distinct...should they be grounded to earth in different places?
jben quote-
"The N and G for the solar circuit are distinct from those for the feeder circuit (different sizes, different overcurrent device) and they do indeed terminate in the sub in the diagram."