grounding a sub panel at a separate building

Status
Not open for further replies.

dia480

Member
do I carry the grounding/bonding electrode wire to the new subpanel in a seperate outbuilding or do I have to drive a new ground rod and then re-bond the whole thing like a new service?

[ June 06, 2003, 11:31 PM: Message edited by: dia480 ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: grounding a sub panel at a separate building

A second building fed by a feeder always requires a grounding electrode system. If there are no conducting paths, other than the feeder circuit conductors, between the two buildings, you are permitted to install the feeder without an equipment grounding conductor and rebond the neutral at the second building. If there is any type of conducing path between the building, you must have an EGC and the neutral is not rebonded.
Don
 
Location
Florida
Re: grounding a sub panel at a separate building

What would be an example of the conducting paths. Would metal water piping be one of them if the water is fed from the other building and not a seperate supplied water service?
 

jro

Senior Member
Re: grounding a sub panel at a separate building

If its a sub panel that is fed out of a main panel your grounding would be either your conduit or other recognized method Art.250.118, you don't treat it as a seperate service, all your main grounding should be at the first point of disconnect, at the sub-panel you would not bond the grounded conductor.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: grounding a sub panel at a separate building

Originally posted by jro:
at the sub-panel you would not bond the grounded conductor.
Normally that would be true, but for a feed to a separate building you will have to bond the neutral to the ground if you chose not to run an equipment grounding conductor which is allowed if as Don pointed out there are no other metallic paths between buildings.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: grounding a sub panel at a separate building

dia480

You have two ways to handle a feeder between two buildings.

With both methods you need a grounding electrode as required by 250.32

Method one

Run separate ungrounded, grounded and grounding conductors from one building to the other, do not bond the grounded conductor to the grounding conductor. Put in a grounding electrode at the second building and connect it to the grounding conductor.

Method two

If there are no other metallic paths between buildings (water pipes, coax cables, gas lines, whatever) you are allowed to run just the ungrounded and grounded conductors out the to second building.

In this case you must bond the grounded conductor to the panel enclosure and again install a grounding electrode connected to the grounded conductor.

Hope this helps, Bob

[ June 07, 2003, 12:51 PM: Message edited by: iwire ]
 

pierre

Senior Member
Re: grounding a sub panel at a separate building

Hello dia480,
If this is a new installation that will or is being installed, I would 'advise' the installer to run the equipment grounding conductor (EGC) with the feeders (even though it is not required), and wire the same way as any 'subpanel'. Regardless of how you run the feeders, you are REQUIRED TO INSTALL A GROUNDING ELECTRODE SYSTEM as per 250.32(A). The purpose of the grounding electrode system at the 2nd building is for lightning protection. The grounding electrode conductor is connected to the grounding bus.

Good Luck,
Pierre
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: grounding a sub panel at a separate building

Ras,
Water piping, gas piping, and communications circuits are all examples of metallic paths other than the feeder circuit conductors that would be conductive paths between the buildings.
Don
 

tom baker

First Chief Moderator
Staff member
Re: grounding a sub panel at a separate building

Pierre, "I would 'advise' the installer to run the equipment grounding conductor (EGC) with the feeders (even though it is not required)," excellent advice. In Washington State, it is not allowed to reground the neutral at a separate building or structure (state code), effective May 23, 2003.

And a sepatate building does not always require a grounding electrode system. A building with a single branch circuit does not require a GES, and Art 210 states a multiwire branch circuit can be considered a single branch circuit, IE a 12-3 w/G to a garage does not require a GES.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: grounding a sub panel at a separate building

If I was asked to do this I would not even think of not running a EGC, just out of habit from doing subpanels inside.

I do have a question for the theory guys though.

Wouldn't leaving the EGC behind and bonding at the second building be a good idea as that will create the shortest path for branch circuit fault clearing?

Say the buildings are 300' feet apart, by bonding at the second building you take 600' of conductor out of the circuit.

What is the down side of this method, other than the likelihood of a conductive path being established later?

Bob
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: grounding a sub panel at a separate building

Bob,
Say the buildings are 300' feet apart, by bonding at the second building you take 600' of conductor out of the circuit
The current still has to travel back to XO at the transformer to clear the fault. The only difference is that when you have an EGC the fault clearing path is via this conductor and when you rebond the fault clearing path is via the grounded conductor. The lenght of the fault clearing path doesn't really change, but by bonding at the second building you do have a lower impedence fault clearing path because the path will be via the the feeder grounded conductor and not the smaller EGC.
Don
 

bennie

Esteemed Member
Re: grounding a sub panel at a separate building

The down side is the cost of the fourth wire when three will do the same thing better with less impedance.

Do you think some code panel members worked for the wire industry?
 

tom baker

First Chief Moderator
Staff member
Re: grounding a sub panel at a separate building

Bennie, the impedance should be the same if all circuit conductors are in the same raceway. the change was made to prevent neutral current on metal raceways and other conductive paths which would be in parallel.Mike Holts Illustrated Grounding and Bonding 2002 text has details and graphics of this dangerous practice. I'd like to send you a copy of his text.
 

bennie

Esteemed Member
Re: grounding a sub panel at a separate building

Tom: I should have been more clear with my thoughts. I am referring to SE cable, in residential applications, and outbuildings with no equipment ground.

Most outbuildings are either in PVC, direct burial USE,URD, or overhead spans. Very few will have metal conduit for the feeder.

The neutral conductor will be larger than an equipment ground conductor and will clear a fault quicker. Two ground conductors are not needed. One ground conductor is not dangerous. There is thousands of them in use.
 
Location
Florida
Re: grounding a sub panel at a separate building

Tom, If the multi wire branch circuit is attached to 2 20a breakers for lets say lights and recp's is that not 2 circuits just sharing a neutral? :confused:
 

gwz2

Senior Member
Location
Indiana
Re: grounding a sub panel at a separate building

Remember, multiwire circuits are ungrounded conductors with a voltage between the ungrounded conductors and also voltage between each ungrounded conductor and the grounded conductor ( neutral ).

Just to clarify that two or more ungrounded conductors of the same phase ( or leg of a 1? source) and an grounded conductor is NOT a multiwire circuit.
 

jro

Senior Member
Re: grounding a sub panel at a separate building

Iwire I belive there is a misunderstanding as to what an EGC is, and forgive me if I misunderstand your qoute, Art 250.118 Types of Equipment Grounding Conductors, an EGC is not always going to be a wire, although it is good practice to run an EGC wire within a raceway, but as Bennie states the cost of adding a fourth wire, Example:1phase 120/240v, 2 hots 1 nuetral 1 EGC, can add to the total cost of the job that could mean the differance between winning or losing a bid, and I am clear on the part of Art. 250.32 (B) (2) when no grounding electrode is present, then you would bond the nuetral at the outbuilding Sub-Panel to the can, Art 250.32 gives a clear answer to the grounding requirments for two or more buildings or structures, but say at the outbuilding I drive a ground rod and take an EGC to say cold water, would I still need to bond the nuetral to the EGC or would the added EGC violate any codes. :)

[ June 08, 2003, 10:20 AM: Message edited by: jro ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: grounding a sub panel at a separate building

Hi jro, I am not sure what you are getting at.

EGC = equipment grounding conductor

GEC = grounding electrode conductor

If the buildings have a feeder between them the second building will always need a grounding electrode.

But you are not required to bring out the EGC from the first building to the second, if there are no conductive paths between buildings.

You could run PVC raceway 2 hots and the neutral
between the two buildings and be code compliant, but you would have to rebond the neutral to the can.