You have two ways to handle a feeder between two buildings.
With both methods you need a grounding electrode as required by 250.32
Method one
Run separate ungrounded, grounded and grounding conductors from one building to the other, do not bond the grounded conductor to the grounding conductor. Put in a grounding electrode at the second building and connect it to the grounding conductor.
Method two
If there are no other metallic paths between buildings (water pipes, coax cables, gas lines, whatever) you are allowed to run just the ungrounded and grounded conductors out the to second building.
In this case you must bond the grounded conductor to the panel enclosure and again install a grounding electrode connected to the grounded conductor.
Hope this helps, Bob